I am anchoring a 6x6x3/8 angle to a 8" solid grouted cmu wall. The wall is 10ft long as is the angle. The loads are 1200#/ft vertical and 7500# shear (horizontal). I cannot seem to find a anchor to work at any layout dimensions. Any help would be appreciated

shear strength of anchor,Masonry Design

1 Reply
Posted by Ashley Couronalmost 3 years ago
Hilti Verified

Hi Chad,

Within PROFIS Engineering there is a "Calculate All" option within the anchor drop down menu that will calculate all possible anchoring options. I have attached a snippet for your reference. If you would like further assistance, please email your ".pe" file to hnatechnicalservices@hilti.com.

Regards,
Ashley

Profis engineering software