Posted by MAYA SNELLERover 2 years ago
Adhesive rebar anchorage capacity at concrete over metal deck

I have a project that requires a concrete housekeeping pad to be anchorage to the roof concrete over metal deck diaphragm. It is a 2.5" concrete over 3" metal deck (5.5" total). The profis engineering metal deck tool does not have a rebar adhesive option to choose. What is the best way to determine the capacity of the rebar anchorage to the concrete over metal deck.

concrete,adhesive,REbar,Deck,metal

1 Reply
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Maya,

This is currently outside of the scope of Hilti's testing. The engineer of record could consider using engineering judgement and/or on-site testing to account for variability in performance.

Regards,
Ashley