Skip to main content

Adhesive anchor

Posted by  Arashabout 4 years ago
Adhesive anchor

Hello,
Adhesive anchors shall be installed 21 days after pouring concrete per ACI. Is there any product that can be used to install the adhesive anchor earlier than 21 days?

Thank you,

Arash

adhesive anchor,epoxy adhesive

1 Reply
Posted by Ashley Couronabout 4 years ago
Hilti Verified

Hi Arash,
 
For information on anchoring into green concrete, please reference Hilti’s Anchor Product Technical Guide Section 2.1.2 on pages 10-11. Click here to access the guide from Hilti’s website. Information on adhesive anchors installed into concrete that has cured less than 21 days can be found in the attached image. Typically, site testing is recommended to verify the fastening capacity into green concrete applications.

Regards,
Ashley