ADHESIVE ANCHOR INTO CRACKED VS. UNCRACKED CONCRETE

Posted by Steven Russellover 2 years ago
ADHESIVE ANCHOR INTO CRACKED VS. UNCRACKED CONCRETE

I am checking the bond strength of an adhesive anchor, and I noticed that the bond strength increased with cracked concrete and reduced with uncracked concrete. I would expect the opposite to be true. I am wondering why this is the case?

Note:
Cracked Concrete Bond Strength: 87%
Uncracked Concrete Bond Strength: 204%

bond strength,Adhesive Anchor Concrete,Cracked vs uncracked

2 Replies
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Steven,

For further assistance, please email your ".pe" file to hnatechnicalservices@hilti.com so that we may analyze your design file.

Regards,
Ashley

Profis engineering software

Posted by TRAVIS POOLEover 1 year ago

Was there any resolution to this question? Comparing the reports for both cracked and uncracked conditions suggests the answer might be in either the tau variable used in ACI 318-19 eqn 17.6.5.2.1 or cNa (eqn 176.5.1.2a), but I'm also seeing psi_cp,Na using the same variables with different results.

I've attached my .pe file.

bond strength,Cracked vs uncracked