8 and 10 inch pipe penetration through 3 hour wall
Posted by Rebecca Coleabout 3 years ago
I have a block wall that is rated 3 hours. We have a few roof drains that need to penetrate it, one 8" and one 10" pipe. Do you have a 3 hour penetration system that would work for this condition?
pipe penetration,3 hr rated
1 Reply
Posted by Nathaniel Crawfordabout 3 years ago
Hi Rebecca - thanks for using the AskHilti platform. Depending on the type of penetrant you have, Hilti has several listed systems available for larger penetrants through a block wall for a 3-hr fire-resistance rating. If you have a metallic penetrant, I've attached C-AJ-1226 which should work for you here.
The best place to search for additional systems will be through our online portal, the Hilti Construction Platform (HCP). You can register for HCP and utilize the online firestop selector at constructionplatform.hilti.com.
Regards,
Nate Crawford
Lead Fire Protection Engineer - Facade