Skip to main content
Cart

4" PVC pipe penetration thru UL L-528 horizontal assembly

Posted by JV Architectabout 4 years ago
4" PVC pipe penetration thru UL L-528 horizontal assembly

We are looking for a detail for a PVC pipe penetration through a UL L-528 horizontal assembly (wood truss). The pipe is larger than 2" diameter, but not more than 4". It is within the wall cavity and penetrating at the top plate of the wall, through the horizontal assembly. Thanks.

firestop,Horizontal Assembly,PVC Pipe penetration,UL L-528,non-metallic pipe

1 Reply
Posted by Jose Hernandezabout 4 years ago
Hilti Verified

Hello,

We do not have any listing that will specifically call out an L528 floor ceiling assembly. Are listings are more general and just call out L500 series design so they can be used for a variety of L500 designs. I have attached the UL listing for FC-2030 to this response which can be used to address maximum 4" PVC through an L500 series floor/ceiling assembly with an optional gypsum chase wall for the penetration to run through.

If you would like to specific design number called out we would need to address that in an engineering judgement. If that is the route you would like to take I have attached instruction for the Hilti Construction Platform below. This is where you will go to submit for engineering judgement request.

We are proud to announce the launch of the HILTI CONSTRUCTION PLATFORM (HCP), our company’s new engineering service website. This platform will be the home for all of your Fire Protection Design needs. Instead of emailing a PDF form for a request, the platform enables you to create new Engineering Judgment (EJ) requests, submit revisions to previously completed EJs or connect with an FPE on a question. HCP also enables you to track the status of your request.

You can find more information on how to access this new platform here: http://www.hilti.com/ej (US) or http://www.hilti.ca/ej (Canada.) If you have any questions or require assistance navigating the platform, please call Customer Service for help at 1-800-879-8000 (US) or 1-800-363-4458 (Canada.)
 
Along with HCP, Hilti is excited to announce our new mobile app for all your firestop needs: Hilti Firestop Selector. Using the Firestop Selector app gives you easy access to the Hilti Fire Protection Design Team from the jobsite, on the road, or in the office to request a new EJ, an EJ Revision, or a Question anytime, anywhere. You can download the app using the appropriate link below.

Hilti Firestop Selector App – Google Play Store

Hilti Firestop Selector App – Apple App Store

If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.
 
Best regards,
 
Fire Protection Design Team
Hilti North America

L500,gypsum chase wall,L528,Firestop collars,max 4 PVC