3 Hour Head of Wall at PEMB

Posted by JDPover 6 years ago
3 Hour Head of Wall at PEMB

i"m looking for a 3-hour rated head of wall detail for a GWB and metal stud wall terminating against faced insulation at a pre-engineered metal building roof. The UL detail HW-D-0488 has all the components I need, but not a 3-hour rating. Thanks in advance!

3 hour,Head-of wall,Pre-Engineered Metal Building

1 Reply
Posted by Travis Pearceover 6 years ago
Hilti Verified

Hello,

The Hilti equivelant for the HW-D-0488 is our HW-D-0528 (see attached). This is also for 1-hour F-rating. We can address the F-rating through an engineering judgment which will be a detail showing your exact application with the firestop components to maintain the stated ratings.
 
Please see attached for Hilti engineering judgment request form. Please fill out the form and email the completed form with any additional details to usfirestopeng@hilti.com
 
Please include a photo or sketch if possible.
 
If you have any questions, comments, or concerns please feel free to call or email us.
 
Thank you for choosing Hilti as your firestop specialist and have a great day.

Regards,

Travis Pearce
Fire Protection Engineer
 


1 comment on this reply
Posted by Amanda Speranza-Kellyover 2 years ago
Good Afternoon, I have the exact same condition for a project I am working on. Was an engineering judgment provided for the 3hr fire-rated head joint? If yes, how should I proceed to get a copy of the judgment?