Hellow, I'm looking for a 2-hr rated firestop listing for penetration of a 15-inch laundry exhaust duct through a wood frame assembly (UL L538)
Please let me know if that is available, and reach out if there are any questions.
Thank you
Steve Lane, AIA
BAS1S Architecture PC
Steve,
Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs.
While we do have a system for a duct through a wood floor/ceiling assembly, it's designed for a 1-hr. fire-rating and a maximum 10" diameter duct. As such, we can address your application through an Engineering Judgment which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)
Along with HCP, Hilti is excited to announce our new mobile app for all your firestop needs: Hilti Firestop Selector. Using the Firestop Selector app gives you easy access to the Hilti Fire Protection Design Team from the jobsite, on the road, or in the office to request a new EJ, an EJ Revision, or ask a Question anytime, anywhere. You can download the app using the Google Play Store or Apple App Store.
If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance or use the following link to access the How-To Videos for HCP on YouTube: Hilti Fire Protection Software How-To Videos Playlist
Thank you,
Jessica Starks
Lead Fire Protection Engineer