2 Hour Shaft wall UL

Posted by jeff Haglerover 5 years ago
2 Hour Shaft wall UL

I have a 2 hr. shaft wall and there are 3 - 4" conduits in the wall that stick out past my 2 layers and then turn 90 degrees out of the wall and trying to find a way to keep the 2hr. rating. wondering if I can just put 4 layers of drywall as long as the last 2 are uncut? or can the pipe be stuffed and sprayed with a Hilti product.

firestop,Fire stopping,ANSI/UL listed

1 Reply
Posted by Moover 5 years ago
Hilti Verified

Jeff Hagler,

Thank you for reaching out to us. See attached W-L 8098 that matches your field scenario. Please review attached and feel free to reach out to us if you have any questions.
You can reach us on 800-879-8000 for any questions that you may have after reviewing detail.

Regards,

Mo Hassan