2 hour rating of an open-web steel joist and concrete floor system

Posted by STEVEN TUCKERabout 1 year ago
2 hour rating of an open-web steel joist and concrete floor system

I have an existing open web joist framed floor system with a 3 1/2 thick concrete floor slab over metal lath and need a 2 hour floor system rating. We initially specified a gypsum ceiling but there's too much material and equipment in the area. Looking for an applied intumescent solution. The joists are 12” deep with the top and bottom cords (2 each) @ 5/8” diam. With the center web bars ½” diameter. 

intumescent,2 hour rating,open-web steel floor joist

3 Replies
Posted by Michael Vuabout 1 year ago

Hello, I've attached a few systems that have fireproofing as a reference. You will most likely need to reach out to a cementitious fireproofing company to see what your options are. Let me know if you have any further questions.

Thank you,
Michael Vu
Fire Protection Engineering Team
Hilti North America
 
3701 W. Royal Lane, Suite 100 I Irving, TX, 75063
P 1-800-879-8000
usfirestopeng@hilti.com
www.us.hilti.com/firestop


Posted by STEVEN TUCKERabout 1 year ago

Thanks!