I'm looking for a 2-hour rated head of wall detail for a gyp bd and metal stud wall terminating against faced insulation at a pre-engineered metal building roof. The UL detail HW-D-0528 has all the components I need, but not a 2-hour rating. Thanks in advance!
Hello Robin,
Our closest system will be CJ-D-0004 (see attached). Unfortunately given testing in order to achieve the 2 hour rating the roof insulation would need to be removed at the head of wall. Or if the roof insulation must remain in place we can offer a cold smoke seal EJ with no rating. Please see the attached EJ request form for your review. Your request can be submitted to usfirestopeng@hilti.com and we can begin processing an EJ.
Thank You for choosing Hilti as your Firestop Expert!
Best regards,
Matt Baker