1hr tenant wall penetration

Posted by Systems Designerabout 4 years ago
1hr tenant wall penetration

I need a penetration solution for a single A/C refrigerant line set through a 1hr FR office tenant separation wall. The 1hr wall assembly is metal stud and 5/8" FR gypsum wall board

1 hour firestop,fire separation

1 Reply
Posted by Michael Duncanabout 4 years ago

Hello,

Thank you for you question on penetration firestopping. Our most appropriate UL listed system for an HVAC line set running through a 1-HR gypsum wall would most likely be W-L-8085 (attached). This system utilizes the Hilti CP 653 Firestop Speed Sleeve. If you are looking for a different solution, you can always reach out to our Fire Protection Design Team via the Hilti Construction Platform. This can be accessed at hilti.com/ej for the U.S., or hilti.ca/ej for Canada. You can also reach our team through your local Hilti field representative, or you can call in to our customer service department at 1-800-879-8000.

Thank you and please let me know if you have any further questions.

Best regards,

Michael Duncan
Fire Protection Engineer
Hilti

firestop,Penetration,HVAC line set