1 Hr GWB Open Web Joists

Posted by William Gantover 2 years ago
1 Hr GWB Open Web Joists

May I have some guidance for firestopping at a 1-hr metal framed, GWB wall perpendicular to open web steel joists?

Thank you.

fire foam at vertical fire partition,open web joist

2 Replies
Posted by William Gantover 2 years ago

HW-D-0218 is close.

For anyone else looking.


Posted by  Kevin Riechersover 2 years ago

Hello,

Does the attached HW-D-0218 meet your application needs? If your joist has no fireproofing then please go ahead with submitting a new engineering judgment and we can take care of your application needs there.

Please let us know if you have anymore questions.

Thank you,
Kevin Riechers