1 hour rated vertical enclosure system

Posted by DELL LIVINGSTONover 2 years ago
1 hour rated vertical enclosure system

We need a 1 hour vertical enclosure system at a storefront glass (no mullion). We need it to have min. 55 stc too.

1 hour firestop,glass,storefront

1 Reply
Posted by Shazi Shahabiover 2 years ago

Thanks for your firestop request. To treat a joint between a vertical fire barrier and non-rated aluminum curtain wall, generally we can provide Code Evaluation Detail, CED, based on the code language in IBC section 715.4.2. This detail will be subject to the approval of the Authority Having Jurisdiction. Depending on how the interior wall is terminating into the exterior wall, we may have to look into different form of solutions. In order to provide you with a solution, we will need an EJ Request. Please submit your Engineering Judgement request on Hilti Construction Platform using the link below: 
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.) 
 
If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance or use the following link to access the How-To Videos for HCP on YouTube: Hilti Fire Protection Software How-To Videos Playlist
 
Fire Protection Design Team
Hilti North America
 
3701 W. Royal Lane, Suite 100, Irving, TX 75063
P 1-800-879-8000 I F 918-254-1679
E usfirestopeng@hilti.com

www.us.hilti.com/firestop

curtainwall,Code Evaluation Detail,vertical fire barrier,vertical joint