The local fire marshal requires all penetrations be made at a 90 degree angle to the wall. Do you have literature describing an angular wall penetration method?
Hello Rusty,
UL published Guide Information related to Through Penetration Firestop Systems. Looking at page 2 of this document; specifically, the second paragraph under the table on page 2, it states that uninsulated penetrating items that meet all other specifications in a UL design can be installed at any angle.
As for non-metallic penetrations, we have UL System W-L-2340, and W-L-2128. These speak on how to address up to 4” PVC (Sch. 40) plastic piping, ABS plastic piping, and CPVC plastic piping.
Any other penetration would either need to be installed at a 90-degree angle, or we can look at addressing your application through an engineering judgement.
I have attached the UL guide info, UL system W-L-2340, UL system W-L-2128, as well as an engineering judgement request form. If an engineering judgement needs to be requested please fill out the request form and email it back to USFIRESTOPENG@HILTI.COM.
Have a great day and let us know if there are any other questions.
Regards,
Dakota Reid
Fire Protection Engineer