Skip to main content
Cart

What is Condition A Shear and Condition B Shear ? What is Condition A Tension and Condition B Tension

Posted by BIJUMON Nairabout 3 years ago
What is Condition A Shear and Condition B Shear ? What is Condition A Tension and Condition B Tension

I am designing a pilaster with base plate and anchor bolts to support an HSS column. There is a tension force and shear force acting. During the analysis and design using Profise, I found that there are Condition A Shear, Condition B shear, Condition A Tension and Condition B Tension. What these terms indicate ?

shear,tension,Supplementary,reinforcements

1 Reply
Posted by Danielle Filerabout 3 years ago
Hilti Verified

Hi Bijumon,

PROFIS Engineering has two options available for the evaluation of reinforced concrete:

  1. Supplementary Reinforcement: For post-installed and cast-in-place anchors, supplementary reinforcement will not transfer the load to the concrete member but will help to restrain concrete breakout, per the ACI 318-14 Anchoring-to-Concrete provisions. If utilizing this feature, Condition A and Condition B can be chosen for Tension and Shear, which will modify the f-factor and ycp,N (or ycp,Na) used in the concrete breakout calculationIn PROFIS Engineering, the use of supplementary reinforcement will not modify the pullout or pryout capacity calculations; this is not defined in ACI 318-14 Anchoring-to-Concrete provisions. For more information, please reference page 247 in the PROFIS Engineering Design Guide here.
  2. Anchor Reinforcement: For cast-in-place anchors, PROFIS Engineering allows the user to select anchor reinforcement in tension and/or shear to prevent concrete breakout, thus stating that the concrete breakout utilization is 0%. This feature will not be available for post-installed anchors due to the complexity of trying to properly place the anchor in the reinforcement, as discussed in ACI 318-14 Anchoring-to-Concrete provisions. For post-installed anchors, the engineer on the project can use engineering judgment to decide to ignore the concrete breakout calculation based on their knowledge of the reinforced concrete member.

 
Regards,
Dani

supplementary reinforcement,condition A,condition b