In PROFIS, the only choice given for the substrate for the design of anchors in the face of a grout-filled concrete masonry wall is "STRETCHER BOND". ESR-4143, for HIT-HY 270, makes no mention of the whether the wall is laid in running or stacked bond. Am I missing something, or is this just a peculiarity of the software?
Hello,
Hilti anchor tests were performed in stretcher bond and therefore, the ICC ES Reports and PROFIS Engineering only provide data for this condition. It'll be up to engineering judgement if the Engineer of Record would like to use this data as a guideline in stack bond applications. Onsite testing might also be considered to verify anchor performance.
Best,
Sam
Hi,
The previous Hilti response did not claim or state that the ESR contains stretcher bond information. The previous response is providing information not included in ESR-4143 -- that Hilti anchor tests were performed in a stretcher bond configuration. Therefore, all the data for HIT-HY 270 into masonry is based off of testing into stretcher bond; Hilti does not have testing into a stacked bond.
Regards,
Emily