Proof test loads for bolts in shear (DSA)

Posted by JORDAN WOLDERover 1 year ago
Proof test loads for bolts in shear (DSA)

I have a DSA project in the Los Angeles area that requires proof test loads for post-installed anchors per CBC 1910A.5. We are using HAS rods with Hilti HIT-RE 500 V3. Section 19010A.5.4 clearly provides the required proof test loads for tension, but it is unclear what is required for shear. For example, in a sill bolt application, without any applied tension loads. What would be the required proof test load for these conditions without any applied tension loads?

HIT-RE 500 V3,pull test,epoxy anchor,proof test

1 Reply
Posted by Ashley Couronover 1 year ago
Hilti Verified

Hi Jordan,

Please see the below information regarding proof loading. On-site evaluation is typically specified by the engineer on the project, by job specific requirements, or by requirements of the authority having jurisdiction. However, the snippet below shows the revised section of ICC-ES AC308, which discusses the proof loading program necessary for adhesive anchors that require continuous special inspection. Hilti adhesive anchors only require periodic special inspection. Thus, Hilti does not need to have continuous special inspection in their ICC-ES reports. The referenced section below provides a helpful guideline for engineers considering on-site evaluation.

13.3.4 Proof loading program- Where required, a program for on-site proof loading, that is, proof loading program, to be conducted as part of the special inspection shall be established by the engineer or design professional of record and shall conform to the following minimum requirements.

  1. Frequency of proof loading based on anchor type, diameter, and embedment.
  2. Proof loads by anchor type, diameter, embedment, and location.
  3. Acceptable displacement at proof load.
  4. Remedial action in the event of failure to achieve proof load or excessive displacement.

Unless otherwise directed by the engineer or design professional of record, proof loads shall be applied as confined tension tests (4.7.2.3). Proof load levels shall not exceed the lesser of 67 percent of the load corresponding to the nominal bond strength as calculated from the characteristic bond stress for uncracked concrete modified for edge effects and concrete properties or 80 percent of the minimum specified anchor element yield strength (Ase,N * fya). Maintain the proof load at the required load level for a minimum of 10 seconds.

R13.3.4 Proof loading programs are traditionally included in the contract documents to enhance the quality control for safety-related anchor installations. Significant latitude is given to the engineer of record in determining the parameters of the proof loading program, which will depend in large part on the type, size, and quantity of anchors being installed.

For adhesive anchors, the nominal bond strength can be referenced in Section 17.4.5.1 within ACI 318-14 Chapter 17 Anchoring-to-Concrete provisions. Per AC308 Section 13.3.4 above, the nominal bond strength can be calculated using a basic bond strength that utilizes a characteristic bond stress for uncracked concrete conditions, τuncr, which can be referenced from the product Evaluation Services Report for the applicable condition considering drilling condition, concrete condition, and temperature range. The basic bond strength of a single adhesive anchor can be referenced in Section 17.4.5.2 within ACI 318-14 Chapter 17.

For mechanical anchors, a similar approach could be utilized evaluating either nominal concrete breakout strength (ACI 318-14 Section 17.4.2.1) or nominal pullout strength (ACI 318-14 Section 17.4.3), whichever controls for the application. The test should be performed as an unconfined test (in lieu of a confined test for adhesive anchors). Proof load levels should not exceed the lesser of 67 percent of the controlling nominal strength (taking into consideration any nearby edge distances or anchor spacings) or 80 percent of the calculated steel yield strength. For all cases, proof load levels should not exceed 80 percent of the calculated steel yield strength.

The final decision for testing and alterations to the anchor system design is typically made by the engineer on the project. For additional information, please reference ASTM E3121/E3121M Standard Test Methods for Field Testing of Anchors in Concrete or Masonry.

proof loading