Post installed 1/2 dia anchor with 60 ft lb torque.

Posted by John Diebold10 days ago
Post installed 1/2 dia anchor with 60 ft lb torque.

Looking for appropriate 1/2 diameter anchor (1/2-13) for exterior post-installed anchors for a switchboard that requires mounting hardware (as seismically tested) with a torque value of 60 ft. lbs. Fixture holes are 0.625" with a pipe spacer of 2.10 inches. Would a Hilti KB TZ2 anchor be appropriate for this?

maximum torque,outdoor post installed anchor

2 Replies
Posted by Hilti Employee (harvkat)3 days ago
Hilti Verified

Hi John,

Thank you for reaching out. The installation torque required for a ½” SS KB-TZ2 into concrete is 40 ft-lb. Hilti would not recommend exceeding the recommended installation torque or violating any other installation parameters specified in Table 1 of the Technical Guide, as concrete splitting and anchor failure could become concerns.

Ultimately, all design decisions (including anchor selection) are at the discretion of the Engineer of Record (EOR) on the project.

Regards,
Katelyn

KB-TZ2,installation torque

1 comment on this reply
Posted by John Diebold3 days ago
Thank you for the clarification/verification. If the KB TZ2 cannot meet the 60 ft lb torque, then we will need to request they provide a different anchor such as the Simpson Strong Bolt 2 which has a 65 ft lb torque for their 1/2' diameter anchor. The 60 ft lb. torque requirement and anchor size comes from the equipment manufacturer's seismic test approval for this switch board.

Posted by John Diebold10 days ago

Note that the KB TZ2 for the Stainless Steel 1/2" diameter anchor only has 40 ft lb installation torque but 60 ft lb required.
A similar anchor provided by Simpson - Strong Bolt 2 for their 1/2" diameter anchor has an installation torque of 65 ft lb. My question is whether the Hilti KB TZ2 1/2" diameter stainless steel anchor can work with the required 60 ft lbs torque or would it cause the anchor to fail. We had specified Hilti KB TZ2 elsewhere on this project - and this is the first instance of a condition where the Electrical enclosure seismic qualification requires a torque of 60 ft lbs for a 1/2" diameter anchor. This is for an outdoor installation of a NEMA 3 tin - aluminum enclosure.