Posted by Andrew Rogersabout 4 years ago
In other than hazardous locations, is there any requirement that the interior of an electrical conduit that runs between floors be filled with firestop?
Fire stop in electrical conduit
2 Replies
Posted by Chase Hellanabout 4 years ago
Hello firestopping within an open ended conduit will be required where it penetrates through a rated assembly (concrete floor, gypsum wall, etc). This is because there will still be an opening if it not firestopped by the proper means. Therefore yes, if an electrical conduit is running through a fire rated floor and is open ended it will need the be firestopped inside of it. If the conduit is continuous between rated assemblies it would not be required to be filled with firestopping material.
Thank you,
Chase Hellan
Fire Protection Engineer
2 comments on this reply
Posted by Chase Hellanabout 4 years ago
Typically yes. I have Attached a Hilti UL listed system W-L-7277 that shows the termination and firestopping of the conduits inside of an electrical panel.
Posted by Andrew Rogersabout 4 years ago
If that conduit terminates in an enclosure, an electrical panel for example, does your response still apply. If so, could you provide a measure of Code related substantiation?