How does the nut friction factor affect the installation torque in the MPII for epoxy anchors?

Posted by Chad Allenover 2 years ago
How does the nut friction factor affect the installation torque in the MPII for epoxy anchors?

For the Hilti HY 200 V3 epoxy, each size of anchor lists a maximum installation torque for threaded rods. For example, a 5/8" threaded rod shows a maximum installation torque of 60 ft-lb. What nut friction factor is this based on? Is it the same as ACI 355.4-19 which uses 0.2 for normal threaded rods without lubricants or friction-reducing coatings, or a different value?

What I specifically want to know, is does the installation torque needs to be reduced if a lubricant is used? I read in another ask Hilti article (https://ask.hilti.com/question/the-effect-of-over-torquing-a-chemical-anchor/muwleo) that over-torquing an epoxy anchor can cause micro-fractures and overstrain the epoxy and result in a reduced load. Do I need to take this into account with a lubricant which reduces the nut factor? And if so, what nut factor was used for the maximum installation torque in the MPII?

epoxy bond,installation torque,friction

1 Reply
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Chad,


The maximum installation torque was found through testing. Additionally, Hilti does not have any testing if a lubricant is used with the nuts. However, it will be up to the engineer of record on the project to determine if a lubricant is suitable to be used for a specific application. If you would like to discuss your application further, please reach out to us at hnatechnicalservices@hilti.com or give us a call at 877-749-6337.


Regards,
Ashley


installation torque