Hilti HIT-HY 270 Spacing Reduction

Posted by BARRY BANDover 3 years ago
Hilti HIT-HY 270 Spacing Reduction

When I run an analysis on six threaded rods in two columns and three rows at 16" on center, Profis output indicates a spacing reduction factor of 0.579. When I look at ICC-ES ESR-4143, Tables 3A and 3B I get an interpolated reduction factor of 0.76. Are we supposed to use a spacing reduction factor for vertical and horizontal spacing so that the actual reduction factor for spacing with 16" on center horizontal and vertical is 0.76*0.76=0.579? If this is correct, it is not clear in the documentation that the spacing reduction factor has to be the product of horizontal and vertical spacing reduction factor.

HIT-HY 270,spacing reduction factor

1 Reply
Posted by Samantha Burtover 3 years ago
Hilti Verified

Hi Barry,

Per ESR-4143, Tables 3A and 3B, Footnote 6 states that load reduction factors are multiplicative. When creating a PROFIS Engineering example with the below parameters, the software specifies the most utilized anchor on page 4 of the design report. In the attached sample, Anchor 1 is the most utilized and would have spacing reduction factors due to the influence of Anchors 2 (horizontal) and 4 (vertical). For a ¾” threaded rod with HIT-HY 270 spaced 16” o.c., the reduction factors are 0.7609*0.7609 = 0.58 (to match PROFIS Engineering). 

Best,
Sam

Profis engineering software,Masonry Design