GC changed shaftwall construction to UL U408 wall assembly for exterior wall. There is an adjacent building next to this wall, so the exterior sheating is inaccessible from the outside. Since this is not a C-H stud, how should drywall joints be treated at the inaccessible outer layer?
Kim,
Unfortunately, this falls outside the scope of firestop. The intent of firestop is to restore the rating between two rated assemblies; however, your application is a butt joint in a gypsum wall, which would need to be addressed with mud and tape per the UL design of the wall. Firestop is not designed to replace mud and tape, so this would be a question better suited for the wall manufacturer.
Thank you,
Jessica Starks
Fire Protection Engineer