Clearance around steel members that are protected with Intumescent Fireproofing

Posted by NICK FICAROover 3 years ago
Clearance around steel members that are protected with Intumescent Fireproofing

Is there a rule of thumb clearance we should allow between a protected member and adjacent construction? For instance, if we are using intumescent coating to protect a column, how much clearance should we give for the coating to expand? Can the adjacent materials be built tight to the member?

clearance,Intumescent Fireproofing

2 Replies
Posted by Jose Hernandezover 3 years ago
Hilti Verified

Hello,

The rule of thumb for our products will be a need for minimum 2" of clearance to allow for the intumescent fireproofing to char and form the proper thermal barrier.

Where this is impeded due to adjacent fire-resistance rated construction, we might be able to provide an alternative engineering judgment solution. For more information about the engineering judgement, please provide an architectural detail of the condition and a description of the issue to USSPEng@hilti.com.

Thank you,
Alex Hernandez
Fire Protection Testing and Projects

clearance,expansion,IFRM,2 Rule,Char

Posted by NICK FICAROover 3 years ago

Thank you for your response.