Beam Upset into Concrete Composite Deck

Posted by Edward Kimabout 4 years ago
Beam Upset into Concrete Composite Deck

I am working on a project in which high ceiling heights are desired, but such goals happen at locations where there is a roof right above it, for which the assembly is quite deep; thus creating a rather tight ceiling cavity between the concrete deck and the ceiling construction. I am working with the team in considering upsetting the beam into the concrete thickness of the composite deck assembly. Snapshot of working detail provided for reference.

I've searched for a number of test assemblies, and it seems that this kind of condition is not one that is usually seen. So I am wondering if there is a test (floor-beam, column, etc.) that is most relatable to the kind of detail in the snapshot.

Please let me know what your thoughts are when you see this.

Thank you.

steel deck,concrete floor,Intumescent coatings

1 Reply
Posted by matthew winstonabout 4 years ago
Hilti Verified

Hello Edward,

Thanks for reaching out. Depending on your local code requirements there may be prescriptive language that address concrete encasement of steel members. Chapter 7 of the International Building Code has such requirements.

It may be possible to provide a detail that combines the method of concrete encasement with spray-applied intumescent fire resistance coatings like All Weather High Build of Fire Finish 120 . If you think this solution would help, please reach out to us at usspeng@hilti.com to start the engineering judgment process.

Best Regards,

Matthew Winston

beam,Intumescent coatings,fire resistance