Posted by Richard A Ehlertalmost 7 years ago
Acceptable Hole Cleaning

I've seen contractors clean out holes with water and then blow them out with air. Is this acceptable, and does it impact installed strength?

Cleaning,Installed Strength

2 Replies
Posted by PARIS STANTONalmost 7 years ago
Hilti Verified

Rick,

Hilti injectable adhesive anchors require compressed air that is delivered at a minimum of 90 psi and 3.5 cfm as indicated in the Instruction for Use. Furthermore, the published load values in our technical documents are based on the 2x2x2 (blow-brush-blow, 2 times) cleaning procedure. The Hilti Safe Set which incorporates our hollow drill bit and vacuum system may be an alternative to the 2x2x2 procedure and will be included in the applicable product technical documents and Instruction for Use. For more information regarding the effects of improper hole cleaning on the capacity of the anchor, please refer to this video.

Paris

hole cleaning,Adhesive Anchors

Posted by PARIS STANTONalmost 7 years ago


Hi Richard,

The hole cleaning method will depend on the type of anchor and manufacturer. In order to ensure you are following the proper hole cleaning and installation methods, please refer to the Manufacturer Printed Installation Instructions for the specific product you are installing.

Regards,
Paris

hole cleaning

1 comment on this reply
Posted by Richard A Ehlertalmost 7 years ago
That's not an answer. Since the webinar addressed epoxy or adhesive anchors, I was looking for a response relevant to those types. I was also hoping that someone could provide some background data, in lieu of just referring to Installation Instructions. Have we lost the ability to respond to anything outside instructions? Apparently so. Rick